250.24(C)(1) - last sentence

Status
Not open for further replies.

dana1028

Senior Member
This last sentence has me puzzled.

"The grounded conductor of a 3-phase, 3-wire delta service shall have an ampacity not less than that of the ungrounded conductors."

I understand the ampacity part - but how do you have a '3-wire' service with 3 phases and a grounded conductor?

[This was new language in 2002 but I never paid any attention to it before.]

Thanx for any enlightenment.
 
Just to reiterate: Let's say "a 3-wire service including a grounded conductor."

I looked in Philip Simmons 'Electrical grounding & Bonding' - he has a color illustration showing the 3-wire system consists of red, black, and white phase conductors - the white phase conductor serves the dual purpose of also being grounded.

Did I get that right?
 
I looked in Philip Simmons 'Electrical grounding & Bonding' - he has a color illustration showing the 3-wire system consists of red, black, and white phase conductors - the white phase conductor serves the dual purpose of also being grounded.

Did I get that right?
Basically, yes.

Just as with a typical 120/240 1ph service, the grounded conductor is to be bonded with the usual EGC/GEC stuff, colored white, and otherwise treated like any other circuit conductor, which it is.

The grounded conductor should never be fused, but may be switched with switches, disco's, or 2- or 3-p breakers. It's a basic 3ph system that just happens to have one circuit conductor grounded.
 