I have an installation with multiple service disconnects rigidly connected by a metal wire way and rigid conduit. I don't believe this meets the requirments of being a "single assembly" mentioned in 250.24 (C) Exception 1. The grounded service conductors are currently brought to each service disconnect but not conncected to each enclosure. They may be connected to the c/t enclosure which is bonded through the metal wireway to the service disconnect enclosures.
I also do not see the connection of the grounded service conductor to the grounding electrode conductor. The only grounding electrode conductor I see goes into the current transformer box. I have not had the utility company open this enclosure yet though.
I don't think this meets the Exception Listed above, but if the grounding electrode conductor is bonded to the c/t enclosure, and the grounded service condutor is connected to it also there, and I go and connect the grounded conductor to the service disconnect enclosure I'm concerned I'm creating parallel neutral current paths on the enclosures, conduits, and metal wireways.
Questions:
1. Does this installation fall under exception one?
2. Do they normally connect the grounded conductors to the grounding electrode conductor inside the c/t cabinet or connect the grounded conductor to the c/t cabinet?
Thanks!
I also do not see the connection of the grounded service conductor to the grounding electrode conductor. The only grounding electrode conductor I see goes into the current transformer box. I have not had the utility company open this enclosure yet though.
I don't think this meets the Exception Listed above, but if the grounding electrode conductor is bonded to the c/t enclosure, and the grounded service condutor is connected to it also there, and I go and connect the grounded conductor to the service disconnect enclosure I'm concerned I'm creating parallel neutral current paths on the enclosures, conduits, and metal wireways.
Questions:
1. Does this installation fall under exception one?
2. Do they normally connect the grounded conductors to the grounding electrode conductor inside the c/t cabinet or connect the grounded conductor to the c/t cabinet?
Thanks!