I have a problem. I'm not doing a very good job explaining the requirements of where the grounded service conductor is connected to a grounding electrode (Article 250.24(a)(1)). If you look at the picture on page 182 of the NEC handbook you will see the illustration of these 3 locations. What is occurring in my neck of the woods is as follows. Some of the local contractors are installing an additional bonding conductor in parallel (usually a #6 green THHN, sometimes a bare) with the grounded conductor. They secure it to the neutral lug in the meter can and run it to the neutral bus in the breaker panel. Then they run it back out either through the point of entry (conduit) or out through the wall.
The NEC identifies for us the three possible points of connections. It does not state you may only use one of these connections.
This to me violates a number of different codes, but because the code does specifically state you can't do this, I'm having a terrible time convincing them they are not installing the service correctly.
I would appreciate any advice on how to resolve this.
Thank you
The NEC identifies for us the three possible points of connections. It does not state you may only use one of these connections.
This to me violates a number of different codes, but because the code does specifically state you can't do this, I'm having a terrible time convincing them they are not installing the service correctly.
I would appreciate any advice on how to resolve this.
Thank you