Good Morning
I attended Mr. Holt's class Friday and Saturday in Orlando and came away with a question.
I have 13,200 volts coming from the utility to a transformer. It is a delta wye transformer.
13,200 to 480. On the secondary side the OX is tied to ground. From the transformer it travels
about 25 feet to a 2000 amp breaker /disconnect. The phase conductors and the ground are the
only wires coming over, does it need to have a neutral (grounded conductor) ?
I do not think so because the ground wire is tied to the transformer and the XO at the transformer
so a fault on the load side anywhere would travel on the ground wire back to the transformer up the XO to the source.
Thank you.