If i have dy 13.8/0.48 kv client transformer located in building's transformer room adjacent to room of main disconnecting mean, Should the tr's terminal bar which is indicated in EXHIBIT 250.15 be located on wall? accordingly neutral and sbj will go out from transformer to this bar.
View attachment 2552086
It needs to attach inside the transformer somewhere but where is somewhat unique to each transformer.If i have dy 13.8/0.48 kv client transformer located in building's transformer room adjacent to room of main disconnecting mean, Should the tr's terminal bar which is indicated in EXHIBIT 250.15 be located on wall? accordingly neutral and sbj will go out from transformer to this bar.
View attachment 2552086
I agree. I dont see mounting the terminal bar exterior of the transformer to be code compliant and seems like a hassle anyway. The transformer likely has a convenient bonding strap built into it.It needs to attach inside the transformer somewhere but where is somewhat unique to each transformer.
You mean the clouded part?Looks to me like that is the grounding electrode conductor that connects building steel (or whatever your electrode is) to the ground terminal with XO and SBJ inside the transformer.
yesYou mean the clouded part?
I concur.Looks to me like that is the grounding electrode conductor that connects building steel (or whatever your electrode is) to the ground terminal with XO and SBJ inside the transformer.
So, the other GEC goes to triangle rods is for what?
My opinion is the building-steel connections in the clouds are required, and the triangular rod arrays are what are supplemental.So the clouded connections are just supplemental
I would caution against focusing too much on ground resistance values, it realy doesnt matter unless you have a spec to meet. Also, I dont know where you are reading about "deep earth grounding", I thought it might be here, but I dont see that same chart:It's the best arrangement in terms of saving spaces,
View attachment 2552109
It's also mentioned somewhere in Motorola spec as well as the exhibition in NEC,I would caution against focusing too much on ground resistance values, it realy doesnt matter unless you have a spec to meet. Also, I dont know where you are reading about "deep earth grounding", I thought it might be here, but I dont see that same chart:
Just take everything you read from these "grounding consultants" with a grain of salt as they usually peddle mostly snake oil.
It's also mentioned somewhere in Motorola spec as well as the exhibition in NEC,
It's not easy to believe you guys an disregard others.
Oh believe me I know. Especially when it's high dollar engineers that are specing these wacko, triangle ground rod patterns and such.It's also mentioned somewhere in Motorola spec as well as the exhibition in NEC,
It's not easy to believe you guys an disregard others.
It's the best arrangement in terms of saving spaces,
View attachment 2552109