ThreeTenFifteen
- Portland OR
- Electrician
When using a wire type "common grounding electrode conductor" for multiple transformers - How does sizing this common GEC come into play when using ground rods as the electrodes?
250.66(A) - States that a grounding electrode conductor connected to (2) ground rods is not required to be larger than a #6CU or #4AL
250.30(A)(6)(a)(1) - States that a wire type common GEC is required to be a 3/0CU or 250KcmilAL minimum.
Would a 3/0CU GEC to the ground rods (2) be required if the intent is to use this as a "common" GEC for said XFMR's.
Any input is appreciated.