"(A) Grounded Systems. A separately derived ac system that is grounded shall comply with 250.30(A)(1) through (A)(8). Except as otherwise permitted in this article, a grounded conductor shall not be connected to normally non?current-carrying metal parts of equipment, be connected to equipment grounding conductors, or be reconnected to ground on the load side of the system bonding jumper. "
Does the "not" clause above relate to all three listed conditions? Is this read as:
1. ...shall not be connected...,
2. (shall not) be connected to equipment...
3. (shall not) be reconnected...?
If the negative applies to all conditions listed, is this normal convention in the NEC?
Is a bonding jumper then required or not required in a single phase 480V to 120V transformer setup to supply control circuit power. Can the bonding jumper, the grounded conductor, and the grounding conductor all be one source such as a ground bar for the 120V system? Or, in this situation, should a grounded conductor from the source be run with the 3 phase ungrounded conductors?
Thanks again for the help.
Does the "not" clause above relate to all three listed conditions? Is this read as:
1. ...shall not be connected...,
2. (shall not) be connected to equipment...
3. (shall not) be reconnected...?
If the negative applies to all conditions listed, is this normal convention in the NEC?
Is a bonding jumper then required or not required in a single phase 480V to 120V transformer setup to supply control circuit power. Can the bonding jumper, the grounded conductor, and the grounding conductor all be one source such as a ground bar for the 120V system? Or, in this situation, should a grounded conductor from the source be run with the 3 phase ungrounded conductors?
Thanks again for the help.