Exhibit 250.15 NEC Handbook shows the following connections to the XO: GEC, SBJ, SSBJ and Grounded Conductor.
If I run rigid steel conduit between the transformer and the panelboard can I do away with the SSBJ since the conduit will basically do the same thing?
(Also to avoid a parallel neutral scenario)