cdcengineer
Senior Member
I have been reading back in the forums about verbiage changes to the 2011 NEC. I want to make sure I understand the installation of SSBJ. Let's say we have a 480p:208s xfmr which sits next to (indoors) the switchboard (SWBD) it serves. The feeders are (6) sets of 500 AL. The xfmr will have a system bonding jumper installed inside the cabinet. Let's assume this installation is per 2011 NEC.
If the feeders from the xfmr to the SWBD are run in PVC, than a SSBJ can be installed in each raceway sized for the 500 AL per 250.66. There would be no equipment grounding conductor (EGC) installed correct - as the SSBJ is installed in lieu of EGC.
What if the feeders are installed in EMT? Does the non-flexible metal raceway act as the SSBJ?
I have been looking back at engineered drawings received over the years, and typically the engineer will provide a xfmr schedule which shows high and low side feeders and grounding electrode conductor sizing. The secondary feeder is usually sized with an EGC per 250.122. I'm beginning to think that this is being sized incorrectly by many in the industry. Anyone care to provide some input?
Thanks
If the feeders from the xfmr to the SWBD are run in PVC, than a SSBJ can be installed in each raceway sized for the 500 AL per 250.66. There would be no equipment grounding conductor (EGC) installed correct - as the SSBJ is installed in lieu of EGC.
What if the feeders are installed in EMT? Does the non-flexible metal raceway act as the SSBJ?
I have been looking back at engineered drawings received over the years, and typically the engineer will provide a xfmr schedule which shows high and low side feeders and grounding electrode conductor sizing. The secondary feeder is usually sized with an EGC per 250.122. I'm beginning to think that this is being sized incorrectly by many in the industry. Anyone care to provide some input?
Thanks