I have been seeing installs of this set up, 100amp service set overhead on a pole with service disconnect.
Than feeder conductors are ran back up the pole and off the other poles overhead to the remote structure (tower site).
However they are only running triplex,2hots,1neutral. And bonding the neutral at the structure. Even in theory I don’t see a problem because there are no other metallic connections between the service and tower site.
But I believe it is pretty clear that one would have to run a 4wire over head cable and float the neutral everywhere else as in any other situation.
I know there are exceptions made for installs that were complaint with the current code in which they were installed, but this new.
Im not missing any way around this am I?