When a disconnect is remote from the building as allowed by 250.32(d); does the panel supplied in the remote building still have to be service rated as required by 225.36 or does the equipment just have to be connected to a grounding electrode system?
Yes (except when no)...When a disconnect is remote from the building as allowed by 250.32(d); does the panel supplied in the remote building still have to be service rated as required by 225.36 or does the equipment just have to be connected to a grounding electrode system?
No exception... must be suitable for use as service equipment.This is for a multi-building natural gas storage facility. Most areas are class I division II and hazardous occupancy.
No exception... must be suitable for use as service equipment.