Relating to 250.32 (A), it refers to 250.50 when there is no grounding electrode installed.
250.50 states where no grounding electrode is present, that 250.52(A)(4) through (A)(8) shall be installed and used.
Does this mean that if there is an installation that does not have a grounding conductor in the raceway, that the neutral can be bonded with the grounding electrode that would be installed at the seperate structure? Would this apply to a swimming pool sub panel also?
I have seen this a couple of times over the years and it was brought up at a continuing education class I attended last night. There were differing viewpoints. Looking for clarification
250.50 states where no grounding electrode is present, that 250.52(A)(4) through (A)(8) shall be installed and used.
Does this mean that if there is an installation that does not have a grounding conductor in the raceway, that the neutral can be bonded with the grounding electrode that would be installed at the seperate structure? Would this apply to a swimming pool sub panel also?
I have seen this a couple of times over the years and it was brought up at a continuing education class I attended last night. There were differing viewpoints. Looking for clarification