Guys,
I have a situation where I have a 1200A 277/480V main switchboard in building 1 that includes a 400A breaker which feeds a panel with 400A main breaker in building 2. The conductors between the two breakers are direct buried in PVC and an equipment ground conductor is included with the three phase wires and a neutral. My interpretation of 250.32 is that at the 400A panel in building 2 the equipment ground wire, as well as the available ground electrode conductors (in this case from the water pipe and a ground rod) at the building are to be landed.
Downstream of the 400A panel (fed from a 200A breaker in the panel) in building 2 is a 480 to 120/208V step down transformer. An equipment ground conductor is being installed to it from the 200A breaker on the line side, and it was planned to have ground electrode conductors installed to it, as well.
My questions are...are separate ground electrode conductors required to be pulled to both the 400A panel in building 2, as well as to the step-down transformer? If the ground electrode conductors at building 2 are pulled to the 400A panel, can an appropriately sized ground electrode conductor be pulled from it to the transformer perhaps in a separate conduit. I would still look to have the equipment ground conductor pulled with the conductors between the 200A breaker and the transformer.
I have a situation where I have a 1200A 277/480V main switchboard in building 1 that includes a 400A breaker which feeds a panel with 400A main breaker in building 2. The conductors between the two breakers are direct buried in PVC and an equipment ground conductor is included with the three phase wires and a neutral. My interpretation of 250.32 is that at the 400A panel in building 2 the equipment ground wire, as well as the available ground electrode conductors (in this case from the water pipe and a ground rod) at the building are to be landed.
Downstream of the 400A panel (fed from a 200A breaker in the panel) in building 2 is a 480 to 120/208V step down transformer. An equipment ground conductor is being installed to it from the 200A breaker on the line side, and it was planned to have ground electrode conductors installed to it, as well.
My questions are...are separate ground electrode conductors required to be pulled to both the 400A panel in building 2, as well as to the step-down transformer? If the ground electrode conductors at building 2 are pulled to the 400A panel, can an appropriately sized ground electrode conductor be pulled from it to the transformer perhaps in a separate conduit. I would still look to have the equipment ground conductor pulled with the conductors between the 200A breaker and the transformer.