if i have a footing, and in that footing is 20' of 1/2" rebar, and there also happens to be a 20' long piece of #4 copper in the footing , aren't they BOTH REQUIRED to be bonded?
are the grounding electrodes described in 250.52(A)(1) through 250.52(A)(6)
actually grounding electrodes if they are not attached to the GEC?
if they are not attached to the GEC are they still "present" ???
if they are not "present" then they don't have to be used, correct???
what about the exception that calls the reinforcement in an existing foundation a "concrete encased electrode"? how can it be an electrode if it is not connected to a GEC?
i thought i understood.... now i am confused again! help!
if i have a footing, and in that footing is 20' of 1/2" rebar, and there also happens to be a 20' long piece of #4 copper in the footing , aren't they BOTH REQUIRED to be bonded?
are the grounding electrodes described in 250.52(A)(1) through 250.52(A)(6)
actually grounding electrodes if they are not attached to the GEC?
if they are not attached to the GEC are they still "present" ???
if they are not "present" then they don't have to be used, correct???
what about the exception that calls the reinforcement in an existing foundation a "concrete encased electrode"? how can it be an electrode if it is not connected to a GEC?