250.50 interpretation

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Does this section only apply to an actual Service as defined by Article 100? Or does it a mean any “building or structure served” with power from a feeder?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
"any"....
You might note in 250.32(A),. separate structures, it references 250.50
 