so this method would replace 2 ground rods???guess you would just termiate #4 at service??????
that is what i was getting at ,by complying to article 250.52(a)(3) you would not need two ground rods...thanks
I understand the context of the question but think Tom hits on an important point. One type of electrode doesn't replace another one. Try not to look at it that way. The code makes it clear that ALL electrodes that are present be bonded together to form the GES. When certain electrodes are not present, the code provides other methods of "creating" an electrode.