What the heck is “each plate electrode shall EXPOSE not less than 2 square feet of surface to exterior soil,” supposed to mean?

I cannot get a visual example of this anywhere. How deep is this supposed to be and what is the code trying to say?
 

HEYDOG

Senior Member
Here is a link that might help!

 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What the heck is “each plate electrode shall EXPOSE not less than 2 square feet of surface to exterior soil,” supposed to mean?
The outer surface of the plate has to expose at least 2 square feet of metal to the earth. A 12"x12"x1/4" plate would exceed the 2 square foot minimum.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Here is an 18 x 18 tinned copper plate electrode
 