Is the conductor between the steel and the water pipe a Supply Side Bonding Jumper?
Ritelec
Thanks.You can call me Rich.
No, it is a service.Do you see anything in the definition of "Supply Side Bonding Jumper" to exclude the conductor depicted between the steel and the water pipe in the diagram?
no. The utility x former is a separately derived system also.
Yes, that's it's reason for being installed, 250.50.Would not the conductor between the beam and water pipe be part of the grounding electrode system (conductor)?
Not so much. What I am getting at is that 250.53(C) states that we follow 250.66, but 250.102(C) requires us to size a large conductor to 12.5% of the ungrounded conductors. The question is, is that conductor between the steel and the water pipe a supply side bonding jumper? I think there is a goof in the definition of Supply Side Bonding Jumper.The conductor between the steel and the water pipe is clearly not a Main Bonding Jumper or a System Bonding Jumper.
Wait........I may be seeing what your getting at........jumper vs conductor.
What I am getting at is that 250.53(C) states that we follow 250.66, but 250.102(C) requires us to size a large conductor to 12.5% of the ungrounded conductors. The question is, is that conductor between
the steel and the water pipe a supply side bonding jumper? I think there is a goof in the definition of Supply Side Bonding Jumper.
It is only a Grounding Electrode Conductor if it connects to the Grounded Conductor at the service. Everything else are jumpers............Is the steal to water pipe a supply side bonding jumper...............I'm going to say no.... it's a grounding electrode conductor.....
I do not see it as a supply side bonding jumper.
I'm going with "Bonding Jumper". My opinion, it's a GEC to the first electrode and bonding jumper after that be it continuous or spliced.wow..................getting real close to just calling it a wire.
So from the neutral to steal it's a conductor (gec) but from steal to water its a jumper (sbj)?
If it were continuous (the wire) from neutral to steal to water pipe, is it still a jumper from steal to water or part of the conductor?
Is the conductor between the steel and the water pipe a Supply Side Bonding Jumper?
No it is an electrode bonding jumper
I'm going with "Bonding Jumper".
No it is an electrode bonding jumper
Why is it not a Supply Side Bonding Jumper?
A Supply Side Bonding Jumper bonds together metal parts that contain service conductors, say, four sets of RMC coming into an open bottom cabinet at a service.Is there such a term?
Why is it not a Supply Side Bonding Jumper?
A Supply Side Bonding Jumper bonds together metal parts that contain service conductors, say, four sets of RMC coming into an open bottom cabinet at a service.
Bonding Jumper, Supply-Side. A conductor, like, installed on the supply side of a service or within a service equipment enclosure(s), or for a separately derived system or somethin', that ensures the required electrical conductivity between metal parts required to be electrically connected and stuff.