Am I correct in my assertion that the following graphic is incorrect?
I believe the objects listed in 250.68(C) exist between a grounding electrode and a GEC.
I believe the objects listed in 250.68(C) exist between a grounding electrode and a GEC.
CMP 5 in response to Comment 5-49 said:Panel Statement: The revised text clarifies that the structural metal is treated the same as the metallic water system. The application from the charging paragraph of 250.68(C) makes it clear that structural metal can be used to connect wire type bonding jumpers or grounding electrode conductors to the structural metal as an extension of the wire type bonding conductor or grounding electrode conductor.