Since Aluminum and Aluminum-Clad wires cannot be used as a ground wire in corrosive environments, what ratings meet the requirements (extruded polymeric covering) so they could be used? XHHW-2? RHW-2? USE? USE-2? Something else? (Yes I know I could just use a copper wire but wanting to know what is available if someone did want to go aluminum) For reference it is to a subpanel by a pool in a weather-rated electrical panel.

Thank You!
 
So this is in a detached building? How long would the GEC need to be to a rod or whatever Electrode is being used?
 
So this is in a detached building? How long would the GEC need to be to a rod or whatever Electrode is being used?
It is not a detached building, it is outside in the open air at the pool equipment area, run through 2" conduit under the concrete and pops up over by the pool pump to run into the NEMA 3R panel. I couldn't see where I'd need a rod since the ground on the subpanel runs back into the main house and a pool isn't a detached building. Homeowner wants to run a pool heater, some outlets, some lights, and maybe a hot tub (separate from the pool), so putting in 125 amps. The pool area is around 2600SF including the pool, all concrete otherwise though.
 
If you have a panel that is not attached to the main building then you need 2 ground rods or some other electrode.
 
If you have a panel that is not attached to the main building then you need 2 ground rods or some other electrode.
So yes, as a detached "structure" it needs the GES. This doesn't get to my initial question which has to do with the grounding wire run from the main panel out to the subpanel though, and the "extruded polymeric" covering that would allow that wire to be Aluminum since it's in a corrosive environment (since it is near a pool). Maybe I'm overthinking the whole "extruded polymeric" thing since pretty much all non-bare wires have some kind of PVC or cross-linked polyethylene covering/insulation around the metal itself, and polyethylene is definitely a polymer.
 
You're referencing the wrong article section then, 250.64 is about the GEC, not the EGC.
 
You're referencing the wrong article section then, 250.64 is about the GEC, not the EGC.
And therein lay my confusion, it's those incredibly similar initialisms that will get you. No problem to run copper wire as the GEC for the subpanel, my question was about using aluminum ground wire for the EGC, but I'm thinking (now that I've got my letters in the right orders) that based on 680.25(A) there is no exception for aluminum (unlike the exception for use of the extruded polymeric covering in the GEC wire).
 
I was getting that idea from 680.25, which says the feeder ground wire has to be copper (bolded below):

680.25 Feeders. These provisions shall apply to any feeder on the supply side of panelboards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment or the source of a separately derived system.

(A) Feeders. Where feeders are installed in corrosive environments as described in 680.14, the wiring method of that portion of the feeder shall be as required in 680.14(B) or shall be liquidtight flexible nonmetallic conduit. Wiring methods installed in corrosive environments as described in 680.14 shall contain an insulated copper equipment grounding conductor sized in accordance with Table 250.122, but not smaller than 12 AWG.
 
I don't believe outdoors is considered a corrosive environment unless chlorine or some other chemicals are stored next to the panel.
 
If you have a panel that is not attached to the main building then you need 2 ground rods or some other electrode.
If it's for Swimming Pools, Spas, Hot Tubs, Fountains, and Similar, Article 680 applies and imposes its own requirements. Two ground rods probably won't suffice.

full disclosure: Article 680 is a little outside my area of expertise.
 
If it's for Swimming Pools, Spas, Hot Tubs, Fountains, and Similar, Article 680 applies and imposes its own requirements. Two ground rods probably won't suffice.

full disclosure: Article 680 is a little outside my area of expertise.

There is no requirement for more than 2 rods for the panel. There are definitely rules for bonding the pool and the perimeter surfaces.
 