Why is liquid-tite flexible metal conduit or steel flexible metal conduit not an approved raceway for GEC and bag wire is?
Example: Indoor installation, 75KVA transformer mounted on tilt-up concrete wall @ 10ft A.F.F with approved wall bracket & isolation pads to reduce noise.
3/4" Rigid conduit to building steel & cold water with uninsulated #2 GEC and
30" of liquid-tite flexible metal conduit only at transformer connection with ground bushing.
Question clarification.
The building electrical specifications require rigid conduit and transformers to be installed on isolation pads to decrease noise.
Primary and secondary feeders to transformers require 30" liquid-tite flex for final connection at transformers to aid in decrease of noise travel. The GEC conduit can not meet building spec and satisfy the code.
Oviously the NEC is the final authority and flex is not an approved conduit for grounding electrode conductor.
Unfortunately the code does not allow exceptions or provide alternatives for this application.
My question is why liquid-tite flex or steel flex is not an approved conduit per 250-64(B)
Other than PVC, the conduit is bonded to limit difference of potential between the GEC and conduit. The grounding electrode conductor is the low impedence path and if uninsulated when installed, where is the hazard? If the liquid-tite flex connector or steel flex connector is insufficient why wouldn't an external bond jumper satisfy.
It seems a loose set screw EMT fitting would pose a greater threat in difference of potential for the GEC installation.