250.64(B)

Status
Not open for further replies.

jimatwork

Member
I have to ground a PDU(150kva trans.) on a raised computer floor.I was running emt then changing over to LFMC(sealtight)with grounding hubs at each end as required.My question is can a grounding electrode conductor be installed in LFMC? 250.64 (B)only lists RMC,IMC,RNC,EMT or cable armor. I can't find the definition of cable armor.

Thanks
 

benaround

Senior Member
Location
Arizona
Re: 250.64(B)

jimatwork,

250.64(B) It does state 'otherwise it SHALL be in rmc,imc,--etc.

LFMC is not on the list.

I have not seen cable armor for a long time now,but it looks like mini mc type armor with a bare copper,solid GEC inside of it.

frank
 

redfish

Senior Member
Re: 250.64(B)

Original question by jimatwork,
Can a grounding electrode conductor be installed in LFMC?
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">If you are just grounding your transformer look at 350.60 in the 2002 Code and that will take you in the right direction. Same article in the 2005 Code,however there is a slight change. Where flexibility is not required, LFMC shall be permitted to be used as an equipment grounding conductor when installed in accordance with 250.102</font>
<font size="2" face="Verdana, Helvetica, sans-serif">:) :)
 

benaround

Senior Member
Location
Arizona
Re: 250.64(B)

redfish,

350.60 has absolutly no value concerning jimatwork's question.

If your just grounding the transformer,then you are installing a GEC.

frank
 

redfish

Senior Member
Re: 250.64(B)

If one were installing a GEC, Then I would agree with benaround. However if one were to need only to ground ones equipment using emt and then xing over to LFMC I would read 350.60 carefully. :) What do you think benaround?

[ July 06, 2005, 09:08 PM: Message edited by: redfish ]
 

redfish

Senior Member
Re: 250.64(B)

jimatwork, are you talking about an equipment ground? :) :)

[ July 06, 2005, 10:43 PM: Message edited by: redfish ]
 