tryinghard
Senior Member
- Location
- California
Is the size of the bus bar ever an issue when terminating in the distribution/panel/switchgear to additional electrodes?
We have an existing concrete building with a CEE, a metal building was added later on top with no record of bonding its frame. Now a transformer is added and the building frame would normally be the electrode. There is no simple route to the building frame for its bond to the CEE but it can terminate at the same location as the existing GEC on the service disconnects bus, would you say this is this compatible with 250.52(A)(2) & 250.64(C)?
We have an existing concrete building with a CEE, a metal building was added later on top with no record of bonding its frame. Now a transformer is added and the building frame would normally be the electrode. There is no simple route to the building frame for its bond to the CEE but it can terminate at the same location as the existing GEC on the service disconnects bus, would you say this is this compatible with 250.52(A)(2) & 250.64(C)?