I was out looking at a project and the Electrician installed a 10' stick of EMT conduit from the Ground bar in the main electrical room to the building steel overhead (for the grounding electrode conductor). The EMT is not connected to anything on either end. He installed a Ground bushing on the bottom end but not on the top. Per 250.64(E) (Ferrous metal enclosures that are not physically continuous from cabinets or equipment to the grounding electrode shall be made electrically continuous by bonding each end of the raceway or enclosure to the grounding electrode conductor).
I think he needs a ground bushing on the top end of the conduit in addition to the one he has already installed.
Let me know your thoughts about this.
Thanks
Ed
I think he needs a ground bushing on the top end of the conduit in addition to the one he has already installed.
Let me know your thoughts about this.
Thanks
Ed