M mpd Senior Member Nov 23, 2013 #1 if a GEC was run thru EMT & a metal enclosure, and meyers hubs were used on each end of the EMT, would that eliminate the need to bond each end of the raceway & metal enclosure to the GEC,
if a GEC was run thru EMT & a metal enclosure, and meyers hubs were used on each end of the EMT, would that eliminate the need to bond each end of the raceway & metal enclosure to the GEC,
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Nov 23, 2013 #2 Imo, the meyers hubs would be compliant assuming that it is listed for bonding and grounding
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 24, 2013 #3 What if they used standard locknuts, aren't they sufficient for bonding and grounding?