250.64 f 3, used with 250.121

Status
Not open for further replies.

Epalmateer

Senior Member
Location
Michigan
Occupation
Electrician
Could you use 250.121 exception hand in hand with 250.64f3? If your egc feeding a sub panel was.large enough to be gec, it would be continuous to a ground bar in the subpanel, and then the wire going from the ground bar in the subpanel to an electrode would be a bonding jumper per 250.64f3? Does this make sense or am I stretching?
 
But you could use a compression splice on that EGC to make it continuous and use split bolt to tap a jumper to the equipment grounding bar in the sub panel. There are other rules that apply that make this difficult to actually accomplish.
 
But you could use a compression splice on that EGC to make it continuous and use split bolt to tap a jumper to the equipment grounding bar in the sub panel. There are other rules that apply that make this difficult to actually accomplish.
Right, iv been trying to figure it out lol
 