I have a 800 amp existing service with no grounding electrode. I need to add a grounding electrode system. The building is already there without a ufer ground and the water main is pvc. I’m going to drive 2 ground rods. 250.66(A) states all I need is #6 for gec to ground rods. So the only other thing I need to be concerned with is bonding to the building steel using table 250.66? Is this right?