250.66 for parallel conductors.

Status
Not open for further replies.

kevins411

New member
Location
Supply NC
What is the approximate area for 1100 kcmil CU? Chapter 9 jumps from 1000 to 1250. EX: Approximate area for 2-500 is larger than the same area for 1000 but smaller than 1250. How can you interpolate this?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not sure I understand the question, what are you trying to interpolate? What in your installation is 1100 kcmil?

Welcome to the Forum. :)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The conductor area for the application of Table 250.66 for conductors larger than 4/0 is the KCMIL area. You simply add the KCMIL of the paralleled conductors to apply Table 250.66.
 

kwired

Electron manager
Location
NE Nebraska
What is the approximate area for 1100 kcmil CU? Chapter 9 jumps from 1000 to 1250. EX: Approximate area for 2-500 is larger than the same area for 1000 but smaller than 1250. How can you interpolate this?


Sent from my iPhone using Tapatalk
Circular mil is a unit of area.

2 x 500 is 1000 last I knew.

?
 