When sizing an grounding electrode conductor, is anything over 1100cu - "3/0" max required ? Or do you have to do the 12.5% of area as required by 250.102(C)(1)
When sizing an grounding electrode conductor, is anything over 1100cu - "3/0" max required ? Or do you have to do the 12.5% of area as required by 250.102(C)(1)
That's it, if it's a GEC it's never required to be larger than #3/0. The 12.5% would apply to system bonding jumpers, main bonding jumpers, etc. Our 4000 amp services have the same size GEC as our 225 kva transformers.