As an electrician and a certified inspector I see the grounding electrode undersized quite often on large sevices. Very frequently the water service is no longer metal but plastic. An example a profession engineer certified that an apt complex with 2 800amp services per building met code with a single #4 Ufer ground and a supplimental #6, 8' ground rod. The only way this service can meet code is with a 3/0 grounding ring, or better a 3/0 ufer, or a grounding plate, but this latter is not allowed in the Dallas area because of the corrosive soils. Note 250.52 (A) (3) concrete encased electrodes states "shall not be smaller than #4 AWG", it can be and should be equal to table 250.66 w/o a water pipe. What is going to happen if the transformer looses it's nuetral, or a large surge or lightning strikes the building? 250.66 clearly states that grounding conductor "shall not be less than table 250.66" My interpitation is that all other forms of the grounding electrode system would be supplimental and not subsitutable for. Any thoughts on this are welcomed ...Greg Eller