250.66A compared to 250.66

Status
Not open for further replies.

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
SO, the way I understand the code, a #6 GEC is the largest GEC needed when setting a seperately derived system GEC?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
SO, the way I understand the code, a #6 GEC is the largest GEC needed when setting a seperately derived system GEC?

I don't think that is correct. The separately derived system grounding electrode should be the nearest of either water pipe electrode or structural metal grounding electrode.

260.66(A) would proscribe a "not larger than" size for pipe electrodes, but not structural steel electrodes.
 