augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 28, 2016 #1 ('-08 Code applicable) Am I reading correctly that other than service raceways as covered in 250.80 and the exception for 2540.112(I), if a rigid elbow in a run of PVC is encased in 2" of concrete it need not be bonded ?
('-08 Code applicable) Am I reading correctly that other than service raceways as covered in 250.80 and the exception for 2540.112(I), if a rigid elbow in a run of PVC is encased in 2" of concrete it need not be bonded ?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Sep 28, 2016 #2 Yes I believe you can either encase it or bury it 18". If this is above ground it may be easier to bond it then encase
Yes I believe you can either encase it or bury it 18". If this is above ground it may be easier to bond it then encase