J jes25 Senior Member Location Midwest Occupation Electrician Mar 14, 2006 #1 How do you size the bonding jumper for this article, if I was to use bonding bushings.
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Service Manager Mar 14, 2006 #2 Line side of disconnect: Table 250.66 Load side of disconnect: Table 250.122 Although, I don't see it spelled out. Seems as though I recall Ryan having a proposal in for something along these lines.
Line side of disconnect: Table 250.66 Load side of disconnect: Table 250.122 Although, I don't see it spelled out. Seems as though I recall Ryan having a proposal in for something along these lines.