A service lateral from a POCO transformer terminates in a meter then from that meter goes to the panelboard. Where the service lateral enters the meter a rigid conduit is used with a locknut on both sides of the meter enclosure. Does this violate 250.92(B)? I would say yes, but it appears that's how some electricians do it and get away with it. I would say even with the (2) locknuts you still need a bonding bushing or a locknut that is rated for bonding (includes a screw). I might be answering my own question as it states plain as day that standard locknuts cannot be the sole means for bonding.