Lets say I have a service lateral to a dwelling in PVC conduit. This terminates at meter enclosure back-to-back with the service main and panelboard inside the garage. The GEC originates from the main enclosure and is sleeved in PVC and all other wiring is NM cable. Is there an "accessible means external to enclosures for connecting intersystem bonding and grounding electrode conductors"?
Do those little clamp-on devices attached to the outside of the meter enclosure by the utility companies qualify? Is this really their external and accessible means at the service equipment?
Lets say I have a service lateral to a dwelling in PVC conduit. This terminates at meter enclosure back-to-back with the service main and panelboard inside the garage. The GEC originates from the main enclosure and is sleeved in PVC and all other wiring is NM cable. Is there an "accessible means external to enclosures for connecting intersystem bonding and grounding electrode conductors"?