250.94
chris kennedy
Miami Fla.
Retired electrician
Remove the word 'existing' from the exception.
Replace the word 'exists' with "are installed" to the exception.
Substantiation, the providing utilities demarks are rarely at the service in dwellings or other structures we have built since we adopted the 2008. Everything is UG here in new construction and the demarks are installed indoors to prevent tampering.
I know the substantiation needs tweeking.
Let's see what it looks like,
Exception: In (removed) buildings or structures where any of
the intersystem bonding and grounding electrode conductors
required by 770.100(B)(2), 800.100(B)(2), 810.21(F)(2),
820.100(B)(2), and 830.100(B)(2) are installed, installation of the intersystem
bonding termination is not required. An accessible
means external to enclosures for connecting intersystem bonding
and grounding electrode conductors shall be permitted at
the service equipment and at the disconnecting means for any
additional buildings or structures by at least one of the following
means:
I would say that since it makes sense to me, the CMP will kill it.