NEC 250.97 I have 480/277V three phase system. In switchboard let’s say I drill hole to put metallic conduit in so that they are right size. So there are no knockouts being used. Would I still have to follow 250.97?


Sent from my iPhone using Tapatalk
 

bwat

EE
Location
NC
Occupation
EE
Yes of course... but most likely the exception would apply to you and you’ll have to use the permissible methods listed under that.
 