Hello,
Been thinking about something.
When sizing a circuit for a thermally protected motor, from what I understand the ocp can be up to 250% of the hp (current)
So I read here..
T430.248 1.5HP @ 230 volt = 10 amps
T430.52 10 amps * 250% = 25 amps Maximum cb.. so that works.
Not sure the hp but... a 9 amp motor x 2.5 would be 22.5 amps. A 25 amp breaker would be too high.
So the question is, a 1/2 HP motor at 4.9 amps * 2.5 = 12.25 amps. Even though a 15 amp breaker is the next size up, wouldn't it be too high as the 25 amp was on the 9 amp motor above?
Thank you