When sizing a 2500 amp service am I correct in using the 90 degree column and using the adjustment factor of .8 because I have more than 3 current carrying conductors in a raceway?
TIA
TIA
27hillcrest said:When sizing a 2500 amp service am I correct in using the 90 degree column and using the adjustment factor of .8 because I have more than 3 current carrying conductors in a raceway?
TIA
Dennis Alwon said:if you do 8 conduits you would only need 350 Kcm. The 350 Kcm are good for 310 amps
310 amps x 8 = 2480amps
No need to count the neutral
Just make sure your calculated load is less than 2480 and your good to go.
raider1 said:That depends on if there is a single overcurrent device for the service disconnecting means. 230.90(A) requires that the overcurrent device be rated not higher than the allowable ampacity of the conductor. So if the OPer has a 2500 amp breaker protecting the service conductors the ampacity of the conductors must be equal to or greater than the overcurrent protective device.
Chris
Where the conductor rating does not correspond to the standard ampere rating of a circuit breaker or fuse, the next-larger-size circuit breaker or fuse may be used, provided its rating does not exceed 800 amperes, as permitted in 240.4(B)(3). See 240.6 for standard ampere ratings of fuses and circuit breakers.raider1 said:That depends on if there is a single overcurrent device for the service disconnecting means. 230.90(A) requires that the overcurrent device be rated not higher than the allowable ampacity of the conductor. So if the OPer has a 2500 amp breaker protecting the service conductors the ampacity of the conductors must be equal to or greater than the overcurrent protective device.
Chris
cripple said:Where the conductor rating does not correspond to the standard ampere rating of a circuit breaker or fuse, the next-larger-size circuit breaker or fuse may be used, provided its rating does not exceed 800 amperes, as permitted in 240.4(B)(3). See 240.6 for standard ampere ratings of fuses and circuit breakers.
Exception No. 2: Fuses and circuit breakers with a rating or setting that complies with 240.4(B) or (C) and 240.6 shall be permitted.
cripple said:Where the conductor rating does not correspond to the standard ampere rating of a circuit breaker or fuse, the next-larger-size circuit breaker or fuse may be used, provided its rating does not exceed 800 amperes, as permitted in 240.4(B)(3). See 240.6 for standard ampere ratings of fuses and circuit breakers.
Exception No. 2: Fuses and circuit breakers with a rating or setting that complies with 240.4(B) or (C) and 240.6 shall be permitted.
Dennis Alwon said:Actually you make a good point. At 2480 amps for the 350 kcm I was talking about then I cannot go to a 2500 amp breaker. I would have to use 400 KCM conductors.
raider1 said:Correct, but your original design with 350 kcmil would work if you had 2-6 overcurrent devices constituting your service disconnecting means, in accordance with Exception #3 to 230.90(A).
Chris
Dennis Alwon said:Yes, but I was thinking only one--doh...
the size of the service is not relevant.27hillcrest said:When sizing a 2500 amp service am I correct in using the 90 degree column and using the adjustment factor of .8 because I have more than 3 current carrying conductors in a raceway?