Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
House Dist is feeding House Mech but they are showing (8)sets of 4 #600’s in EMT with THHN. Distance is 400’. Seems like overkill asthis give about 3300 amps not considering voltage drop. Am I missing something? Thanks.



 

Attachments

  • House Dist & Mech- Roof Schedule.jpg
    House Dist & Mech- Roof Schedule.jpg
    38 KB · Views: 0

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
sub panel appears to be labeled "Mechanical-Roof". Is the conduit routed across the roof ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
House Dist is feeding House Mech but they are showing (8)sets of 4 #600’s in EMT with THHN. Distance is 400’. Seems like overkill as this give about 3300 amps not considering voltage drop. Am I missing something? Thanks.

Sounds about right. This is from the Southwire VD calculator: 6 conductors per phase utilizing a #1000 Copper conductor will limit the voltage drop to 4.94% or less when supplying 2500.0 amps for 400 feet on a 208 volt system.
 