I am thinking of adding shunt trip ground-fault module. Is there anything in the code that prohibits this? What other options are there other than replacing the breaker?
Look at 230.95!I am thinking of adding shunt trip ground-fault module. Is there anything in the code that prohibits this? What other options are there other than replacing the breaker?
Yes, 480V.This is on the service disconnect?
What is the voltage?
That I am not sure.Do they make a GFPE module for a 2500 amp breaker? We usually see a separate unit built into the cabinet.
Same here. That’s why I asked about voltage as the service could be 208.I keep thinking something is missing. Odd that you have a 2500 amp service disconnect that was not GFPE originally. Any detail you can add ??
The switchboard looks old and it is a 480V 3ph, 3W (it appears that there is no neutral bus). It is a solidly grounded neutral system even though the neutral is not carried to the switchboard. Maybe they didn't have GFP because it is 3ph, 3W?I keep thinking something is missing. Odd that you have a 2500 amp service disconnect that was not GFPE originally. Any detail you can add ??
Decades ago this was not uncommon, even though the GFP requirement is actually based on system voltage to ground not how many wires are used.The switchboard looks old and it is a 480V 3ph, 3W (it appears that there is no neutral bus). It is a solidly grounded neutral system even though the neutral is not carried to the switchboard. Maybe they didn't have GFP because it is 3ph, 3W?