25ft Tap Rule for Transformer Question

Status
Not open for further replies.

schicco

Member
Location
New York
My 225Kva transformer Primary-480V & 208V-Secondary is fed from a 350A breaker via (3) 500Kcmil; the transformer then feeds a panel that is located 15ft away via (2) 4#500Kcmil. I can't use the 10ft tap rule, so I am I OK with the 25ft tape rule? Please see attached. Everything is located inside a building.
Thanks a lot

Steve
 

Attachments

  • 1609A-25ft Tap Rule.pdf
    17.6 KB · Views: 3
The biggest problem I see is with 408.36. Once that is addressed, I don't see a problem with the 25ft tap rule.
 
Also, for 800 amps on the secondary of a transformer you need two sets of 600 kcmil, 500 kcmil is not large enough for that application.
 