I posted this yesterday in the general forum but I thought I would try in the engineering section as well to get some perspective.
We installed a 1500LF pull of (3) 1/0 25kV Aluminum conductor with copper concentric neutrals at 240mils insulation. Subsequent to the pull we meggered at 5kV and found 2 phases at approx 20G-Ohms, whereas the 3rd phase was reading only 8G-Ohms. Was wondering if anyone had any experience with this and whether the 8G-ohms is just too low. We will probably hi pot the cable without terminations to see what it does. Just looking for some feedback. I know there's no definitive answer here.
We installed a 1500LF pull of (3) 1/0 25kV Aluminum conductor with copper concentric neutrals at 240mils insulation. Subsequent to the pull we meggered at 5kV and found 2 phases at approx 20G-Ohms, whereas the 3rd phase was reading only 8G-Ohms. Was wondering if anyone had any experience with this and whether the 8G-ohms is just too low. We will probably hi pot the cable without terminations to see what it does. Just looking for some feedback. I know there's no definitive answer here.