25KVa generator to 100amp 3 phase 208volt distro

Status
Not open for further replies.

ftruong

Member
Location
Santa Clara, CA
Hello everybody,

Tomorrow we're supplying supplemental power to a venue for a concert that doesn't have enough stage power for the rig that's being brought in. Therefore we're renting a 25KVa generator. It supplies 3-phase power through the U-V-W lugs. On our 100amp, 208volt distro, it has the corresponding Black Red Blue White Green camlocks for L1, L2, L3, neutral, and ground. Should I pair black to U, Red to V, and Blue to W?

Thank you
 
Hello everybody,

Tomorrow we're supplying supplemental power to a venue for a concert that doesn't have enough stage power for the rig that's being brought in. Therefore we're renting a 25KVa generator. It supplies 3-phase power through the U-V-W lugs. On our 100amp, 208volt distro, it has the corresponding Black Red Blue White Green camlocks for L1, L2, L3, neutral, and ground. Should I pair black to U, Red to V, and Blue to W?

Thank you

Yes, UVW is the same as ABC (black, red, blue) and O is Neutral (white).
I think that nomenclature is IEC. Maybe somebody else can correct me if I'm on the origin.
 