kropjl
Member
- Location
- Cleveland, OH
Hello,
I got an as-built that says that a specified 25kW, 480-3 phase EDH unit has a 60A/3P disconnect switch with 40A fuses. Forgive me, I am a new electrical engineer so if any of my thinking is incorrect here, please let me know where I am going wrong, but the 60A/3P disc. w/ 40AF does not seem plausible to me. The load on each phase for the EDH unit should be 25kW/3 = 8.333kW, which the as-built's panel schedule agrees with. Here is where I may be thinking of things incorrectly, but doesn't a 40A breaker have a load of 40Ax120Vx.8=3840W? A 60A disconnect have a load of 5760W per phase?
Thanks!
I got an as-built that says that a specified 25kW, 480-3 phase EDH unit has a 60A/3P disconnect switch with 40A fuses. Forgive me, I am a new electrical engineer so if any of my thinking is incorrect here, please let me know where I am going wrong, but the 60A/3P disc. w/ 40AF does not seem plausible to me. The load on each phase for the EDH unit should be 25kW/3 = 8.333kW, which the as-built's panel schedule agrees with. Here is where I may be thinking of things incorrectly, but doesn't a 40A breaker have a load of 40Ax120Vx.8=3840W? A 60A disconnect have a load of 5760W per phase?
Thanks!