hotneutral
Member
- Location
- Florida
I installed power for a gate camera and tapped off of the power for the motor because there was nothing else available anywhere close and the camera draws almost nothing. I come to find out the the gate motor is fed from a transformer taking 277 from the property lighting panel to 120. I have 125 hot to neutral at the camera receptacle but the transformer seems to have a floating ground because I have ~70V H-G and ~50V N-G at the receptacle. Do I need to bond neutral and ground at the transformer?