This is yet another area where the NEC could be clearer. I can cite 2011 215.2(A)(1) as allowing a grounded conductor sized for zero amps unbalanced load (meaning no neutral) for a panel supplying only three phase loads with no neutral connections, but 215.2(A)(2) states, "The size of the feeder circuit grounded conductor shall not be smaller than that required by 250.122..." 215.2(A)(2) could be read to require a neutral in all feeders, even delta. It may not be best practice, but I agree that there is no reason to install a neutral to a panel on a 277/480V system if there is no neutral load, but the actual wording of 215.2(A)(2) in the NEC may make one necessary.
2011 NEC 215.2(A)(2) is interesting. The text was added in the 2005 NEC, but was part of 215.2(A)(1). In the 2011 the text was renumbered to 215(A)(2), but the last line, "Additional minimum sizes shall be as specified in
215.2(A)(2) and (A)(3) under the conditions stipulated.", was not changed to 215.2(A)(3) and (A)(4). The ROPs and ROCs seem to primarily address the grounding conductor, not the grounded conductor, but the title is "Grounded Conductor". I think this section of the NEC needs to be reworked. The typo for the reference to 215.2(A)(2) and (A)(3) is still in the 2014. I find it highly unlikely that 215.2(A)(2) would reference itself for additional requirements.