Hi there,
I have a lead where someone is asking for Generator Backup at a Municipal Water Pump Station. According to the prints, the service is rated 240/480. The Generator Supplier makes Generators that are rated 277/480, but not 240/480. There is also a step-down transformer that transforms the power to 120/240. If most of the 480 loads are 3 phase motors, using a 277/480 Genset probably wouldn't be a problem, however, I would imagine the Transformer is Delta-Delta and it would throw off the voltage for the down-stream loads.
Your thoughts?
I have a lead where someone is asking for Generator Backup at a Municipal Water Pump Station. According to the prints, the service is rated 240/480. The Generator Supplier makes Generators that are rated 277/480, but not 240/480. There is also a step-down transformer that transforms the power to 120/240. If most of the 480 loads are 3 phase motors, using a 277/480 Genset probably wouldn't be a problem, however, I would imagine the Transformer is Delta-Delta and it would throw off the voltage for the down-stream loads.