I have run into a situation where a system that has already been installed is now failing due to lighting strikes. The local utility provides a pad mounted 120/240 transformer (3 phase) and locally there is a 3 phase generator (120/240) connected to an ATS.
There is a need for 480 volt single phase and 277 for fluorescent lighting from the system so a 3 phase 120/240 to 277/480 volt transformer was installed. The 277 volt lights are phase to neural and work fine. (Until a lightning strike occurs in the area) but to supply 480 volts to exterior lighting, phase to phase and a grounding conductor is used to feed light poles.
There is no neutral return path to the distribution panel and the breakers do not trip on the surges on the lines. TVSS devices are installed on the system and sometimes handle the surge but more often do not. In certain situations, the 277 lights on the building are knocked out due to the surges on the phases that are not protected.
I understand that this in not correct since there is no method to return a neutral to allow the breakers to trip.
I am trying to determine the code that would apply here that is possibly violated. (NEC 2005) Since this is a separately derived system as defined in Section 100, and is similar to Exhibit 250.7 in the NEC 2005 Handbook the apparent problem is the system is using 2 legs of the secondary of the transformer to feed a single phase lighting system.
I believe the method of remedying the situation and conforming to code would be to install a single phase 240 to 480 volt transformer in addition to the existing 277/480 volt transformer to feed the exterior 480 volt lights.
Any help on identifying code, verify the thinking on this situation as well as the comment on the possible solution would be greatly appreciated.
There is a need for 480 volt single phase and 277 for fluorescent lighting from the system so a 3 phase 120/240 to 277/480 volt transformer was installed. The 277 volt lights are phase to neural and work fine. (Until a lightning strike occurs in the area) but to supply 480 volts to exterior lighting, phase to phase and a grounding conductor is used to feed light poles.
There is no neutral return path to the distribution panel and the breakers do not trip on the surges on the lines. TVSS devices are installed on the system and sometimes handle the surge but more often do not. In certain situations, the 277 lights on the building are knocked out due to the surges on the phases that are not protected.
I understand that this in not correct since there is no method to return a neutral to allow the breakers to trip.
I am trying to determine the code that would apply here that is possibly violated. (NEC 2005) Since this is a separately derived system as defined in Section 100, and is similar to Exhibit 250.7 in the NEC 2005 Handbook the apparent problem is the system is using 2 legs of the secondary of the transformer to feed a single phase lighting system.
I believe the method of remedying the situation and conforming to code would be to install a single phase 240 to 480 volt transformer in addition to the existing 277/480 volt transformer to feed the exterior 480 volt lights.
Any help on identifying code, verify the thinking on this situation as well as the comment on the possible solution would be greatly appreciated.