277/480 volt generator plant help
dickey79
New member
APO, AE
I'm trying to figure out what the KW will be on a 277/480 volt generator plant. We are putting in a new plant that will be stepped up to 4160 volts after a delta transformer and i know what the amperage is on the 4160 switch but don't know what the KW is. The amps are 350 on the 4160 lines. can someone help please?
If you are trying to size the generator there is a ton of engineering work that needs to be completed on the specifics of the load, but in it's most basic form KW is KW so, ignoring losses, your KW @ 4160 is the same as KW @ 480.
Use a portable power meter and measure on the LV side after commissioning the new plant or check the name plate of the new plant for any power rating.